In a panel with four conductors measuring 500 kcmil, which size of wire can be utilized as a main bonding jumper?

Prepare for the IEC 2A Test with a range of flashcards and multiple-choice questions. Each question includes hints and explanations. Ace your exam with confidence!

The sizing of the main bonding jumper is determined by the size of the largest ungrounded conductor in the system. For a panel with four conductors measuring 500 kcmil, the main bonding jumper must be appropriately sized to ensure effective grounding and bonding.

When determining the appropriate size for the main bonding jumper, the National Electrical Code (NEC) provides guidelines that can be referenced. For conductors in the range of 250 kcmil and above, the NEC indicates that the size of the bonding jumper should be not less than 1/0 AWG copper or 3/0 AWG aluminum.

Given this guideline, the choice of 1/0 AWG is correct because it meets the minimum requirement for a bonding jumper in the presence of 500 kcmil conductors. This size ensures that the bonding jumper can effectively conduct fault current, providing a safety mechanism for the electrical system.

Using a bonding jumper that is too small could potentially lead to overheating or failure during a fault condition, which would violate safety standards and could jeopardize the effectiveness of the grounding system. Thus, 1/0 AWG provides adequate capacity for the task at hand while remaining compliant with regulatory standards.