For a service panel fed with four 3/0 AWG conductors, what is the smallest GEC that can be connected to building steel?

Prepare for the IEC 2A Test with a range of flashcards and multiple-choice questions. Each question includes hints and explanations. Ace your exam with confidence!

The smallest Grounding Electrode Conductor (GEC) that can be connected to building steel, when a service entrance is fed with four 3/0 AWG conductors, is determined by the National Electrical Code (NEC) requirements for grounding conductors based on the size of the largest service-entrance conductors.

According to NEC Article 250.66, the size of the grounding electrode conductor must be sized according to the largest ungrounded conductor. In this case, each of the four conductors is 3/0 AWG, which has a specific ampacity and requires a corresponding GEC size to establish a proper grounding path.

For a 3/0 AWG copper conductor, the minimum size for the GEC connected to building steel is 6 AWG, which aligns with the NEC requirements. The rationale behind this sizing is to ensure adequate protection for the electrical system and safe operation by providing a reliable path to ground.

This is fundamental to ensuring safety in electrical installations, as a properly sized GEC reduces the risk of electrical shocks and enhances the effectiveness of the grounding system in various fault conditions. Therefore, choosing a GEC size smaller than 6 AWG in this context would not meet code requirements and